DiMiTKo
Electrical
- Oct 27, 2009
- 16
Hello! I have a lot of problems with the communication between LDCM modules of three end overhead line. The problem is that I lost receive signal from time to time from 100% to 20-30%, and I receive synchronization error. For example for 24 hours I have 10-15 comm fail signals. I use recommended settings for LDCM in the manufacture manual. I have three end so, I have 6 LDCM modules and three of them are masters, three are slaves. I switched off time synchronization to all of them, and I use Echo mode for differential synchronization. I made loop back test from the other end and i saw that some of them making problem with the communication from time to time. When I made loop back test on the terminals of the LDCM with the short cable all of them was working perfect. I'm not sure about the setting for the power of the signal. I saw that on low power they working better, on high power they generated mpore comm fail signals. The lenght of the overhead line is 17 km and we use average distance LDCM modules. Is there someone who can give me advise where could be the problem. Here on site I have one collegue who mesure the fiber optic and he told me that we have 8db optical budget. It is 2,5 less than the device expect.