healyx
Electrical
- Apr 7, 2009
- 115
Hi All,
I'm using Schneiders free Ecodial program to try and calculate some short circuit currents. I was doing a sanity check on the maximum single phase current (Ik1max) and am a long way off their calculated answer. Can anyone confirm I have this wrong?
The system is:
400V Phase/Phase TN-S or TN-C (doesn't matter)
500 MVA upstream network (Rq = 0.035, Xq = 0.351 - standard ratios).
160kVA transformer (4% impedance, Rt = 11.714, Xt = 42.516)
1x95mm2 Cu PVC cable per phase.
1x95mm2 Cu PVC neutral.
1x35mm2 Cu Earth.
So the system is just a transformer feeding a main switchboard via the 95mm2 cables - run length is 50m.
Ecodial apparently uses the UTE NFC-15-500 guidelines to calculate currents.
For maximum 3 phase short circuit current, according to NFC-15-500, the current (Ik3max) is:
Ik3max = (Cmax x m x Uo)/(sqrt(((Rq+Rt+Rph)^2)+((Xq+Xt+Xph)^2))
Where:
Cmax = 1.05
m = 1.05
Uo = 231 (Ph-N voltage)
Rph = Phase cable resistance = 18.51*50/95 = 9.74
Xph = Phase cable reactance = 0.09*50 = 4.5
So I get Ik3max = 4.895 kA - This is the same as Ecodial - so I must be correctly calculating network, transformer and phase impedances.
I can't work out how Ecodial calculated Ik1max, which should be for a Phase to Neutral fault with 20oC conductors.
For maximum 1 phase short circuit current, according to NFC-15-500, the current (Ik1max) is:
Ik1max = (Cmax x m x Uo)/(sqrt(((Rq+Rt+Rph+Rn)^2)+((Xq+Xt+Xph+Xn)^2))
Where all the parameters are the same with new ones:
Rn = Neutral cable resistance = 18.51*50/95 = 9.74 (same as Rph)
Xn = Phase cable reactance = 0.09*50 = 4.5 (same as Xph). It is basically the same as Ik3max, but with the additional impedance of the neutral return path.
I get an answer of Ik1max = 4.21 kA with Rtot = 31.23 and Xtot = 51.87.
Ecodial gives and answer of Ik1max = 3.57 kA with Rtot = 34.16 and Xtot = 62.50.
I just can't work out where they got the higher impedance from. I have found examples of how to calculate Ik1max on the web and they all concur with my calculation. Can anyone help?
I'm using Schneiders free Ecodial program to try and calculate some short circuit currents. I was doing a sanity check on the maximum single phase current (Ik1max) and am a long way off their calculated answer. Can anyone confirm I have this wrong?
The system is:
400V Phase/Phase TN-S or TN-C (doesn't matter)
500 MVA upstream network (Rq = 0.035, Xq = 0.351 - standard ratios).
160kVA transformer (4% impedance, Rt = 11.714, Xt = 42.516)
1x95mm2 Cu PVC cable per phase.
1x95mm2 Cu PVC neutral.
1x35mm2 Cu Earth.
So the system is just a transformer feeding a main switchboard via the 95mm2 cables - run length is 50m.
Ecodial apparently uses the UTE NFC-15-500 guidelines to calculate currents.
For maximum 3 phase short circuit current, according to NFC-15-500, the current (Ik3max) is:
Ik3max = (Cmax x m x Uo)/(sqrt(((Rq+Rt+Rph)^2)+((Xq+Xt+Xph)^2))
Where:
Cmax = 1.05
m = 1.05
Uo = 231 (Ph-N voltage)
Rph = Phase cable resistance = 18.51*50/95 = 9.74
Xph = Phase cable reactance = 0.09*50 = 4.5
So I get Ik3max = 4.895 kA - This is the same as Ecodial - so I must be correctly calculating network, transformer and phase impedances.
I can't work out how Ecodial calculated Ik1max, which should be for a Phase to Neutral fault with 20oC conductors.
For maximum 1 phase short circuit current, according to NFC-15-500, the current (Ik1max) is:
Ik1max = (Cmax x m x Uo)/(sqrt(((Rq+Rt+Rph+Rn)^2)+((Xq+Xt+Xph+Xn)^2))
Where all the parameters are the same with new ones:
Rn = Neutral cable resistance = 18.51*50/95 = 9.74 (same as Rph)
Xn = Phase cable reactance = 0.09*50 = 4.5 (same as Xph). It is basically the same as Ik3max, but with the additional impedance of the neutral return path.
I get an answer of Ik1max = 4.21 kA with Rtot = 31.23 and Xtot = 51.87.
Ecodial gives and answer of Ik1max = 3.57 kA with Rtot = 34.16 and Xtot = 62.50.
I just can't work out where they got the higher impedance from. I have found examples of how to calculate Ik1max on the web and they all concur with my calculation. Can anyone help?