The primary side of a transformer is the side that is supplied with power. The secondary side is the side from which power is taken.
A breaker on the primary side will disconnect the transformer.
A breaker on the secondary side will disconnect the load from the transformer but the transformer will remain energised.
Sometimes transformers are reverse connected.
That is, a transformer that is normally always connected with the high voltage side as the primary may occasionally be used with the low voltage side as the primary.
For example, it is desired to supply power to two small 120 volt pumps. The pumps are 2000 feet away from the panel.
To comply with the code required 3% or 5% maximum voltage drop
The cables would have to be extemely large.
It would be cheaper to buy two identical dry type transformers rated 120/240:600 volts. These transformers are generally use with the 600 volt winding as the primary.
In this example, one transformer would be supplied with 120 or 240 volts and supply 600 volts. The 600 volt winding is the secondary winding.
The second transformer, at the location of the pumps, is supplied with 600 volts. It delivers 120 volts or 120/240 volts. the 600 volt winding is the primary.
Why 600 volts?
At a given load, say 1.2 KVA, the current at 600 volts will be 20 % of the current at 120 volts.
1.2 KVA at 120 volts will draw 10 amps.
1.2 KVA at 600 volts will draw 2 amps. That's a 5:1 ratio.
3% voltage drop at 120 volts is 3.6 volts.
3% voltage drop at 600 volts is 18 volts. That is also a 5:1 ratio. The total voltage drop advantage with the higher voltage is 25:1
When a circuit is long enough that voltage drop rather than ampacity is the determining factor in sizing the cable, you will have approximately a 25:1 ratio in cable size.
With our 1.2 KVA load on #14 AWG wires at 120 volts, we can run about 100 feet with 5% voltage drop.
With our 1.2 KVA load on #14 wires at 600 volts, we can run about 2500 feet with 5% voltage drop.
The point of this is that sometimes there are good reasons to use a transformer in reverse of its normal usage.
Please try to find a way to ask questions of your co-workers.
If you suspect that they are giving you bad information as a joke on you, ask us to verify it for you.
Good luck friend.
yours