Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Pressurization (Smoke Control)

Status
Not open for further replies.

840224

Mechanical
Joined
Jan 31, 2012
Messages
1
Hi,

I am relatively new to Mech. Smoke Control Design and i was hoping someone could help me understand this application better.

I have a room with 518 cubic meter volume. The requirement for zone pressurization system within this building is to maintain this room with a positive pressure not less than 20 pascals higher with respect to outside conditions.

Could someone please advice if it is possible to mathematically calculate the exact volume of outdoor air required to be supplied and extracted whilst maintaining the said pressure condition.

would appreciate your help/advise.

Thanks
Daniel
 
Before you can calculate that, you have to know the leakage on the room.
B.E.

The good engineer does not need to memorize every formula; he just needs to know where he can find them when he needs them. Old professor
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top