Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
I would refrain the pneumatic testing of the PL with 150 Barg . Huge amount of potential energy will be build up and is a real potential danger. Suggest you hydrostatic test .I am worried about the PNEUMATIC TESTING piping of natural gas 150 Barg by N2 or Air because of the many dangers of exploding to person.
yes, there is danger of stored energy in pneumatic test but you can do it. Follow ASME 31.8 pressure test (if you follow the Code). It will give you min and max test pressure and also max permissible hoop stress by Location class.I am worried about the PNEUMATIC TESTING piping of natural gas 150 Barg by N2 or Air because of the many dangers of exploding to person.
Detail : PIPE ASTM A671-CC65 CL.22, 24" x STDx 1000 m
Please help to recommend for performing this test
Thank you. I will persuade the owner to proceed with the hydrostatic pressure test and then dry the piping. Could you please suggest a suitable drying method?Pneumatic test has been suggested due to subsequent drying issues for the pipe after hydotest. However, there are many techniques in vogue for drying of piping after hydrotest. Convince the client regarding the hazards of pneumatic test and furnish the procedures that you would perform to dry the piping after hydrotest. That would solve your problem.
Thank you, broMaybe suradach has already been ejected into space?
not seen since asking the question.
You need to eb careful with the energy equation for pipelines as it doesn't all release in the same instance like say a tank or vessel.
The biggest issue is usually some small bore valve or piece of pipe which breaks off and flies a long way like a bullet.
You need to contact me directly.Thank you. I will persuade the owner to proceed with the hydrostatic pressure test and then dry the piping. Could you please suggest a suitable drying method?
Good spot. I hadn't actually checked, but 150 bar is double the max pressure this pipe can withstand at yield pressure.Am I missing something? That hydrotest pressure on that grade of low yield pipe results in hoop stress almost double the yield strength. This looks like a bomb to me.
What is the design pressure? What is the basis for the test pressure?
It looks to me you have missed a lot. Which Code allows you to do a hydrotest beyond the Yield Strength? The SMYS of the ASTM A671-CC65 CL.22 is same as ASTM A106 Gr. B pipes. How many times we have tested these pipes? All over the place.Am I missing something? That hydrotest pressure on that grade of low yield pipe results in hoop stress almost double the yield strength. This looks like a bomb to me.
You are right.@GD2 What am I missing?
Try running the numbers here.
If we assume this is a B31.8 pipeline, the maximum design pressure is ~875 psig, assuming the highest allowable design factor of 0.8. That results in a hydrotest pressure of 1094 psig, which is about half of the proposed test pressure here (150 barg = ~2175 psig). The proposed test pressure and resulting hoop stress condition are way out of the bounds of any code I'm familiar with.