Dear Eng-Tips Community,
I run a 1200 sq. ft. laser laboratory (12' ceilings). We would like to maintain the air in our lab at ~70 F, with a relative humidity less than about 35%. We have one fume hood in the room, which exhausts about 400 cfm. The remainder of the exhausting is performed by a single large duct leading to a rooftop fan.
Our supply air comes in through diffusers on four separate ducts running in our ceiling. These ducts originate from the hallway outside our lab, where there are four mixing boxes that mix the building hot & cold air. The building cold air is outside air that has been cooled to ~56 F, and the hot air is re-heated building cold air. This system provides good temperature stability (despite our variable heat loads from the lab equipment), but the humidity varies a lot and gets very high when it rains outside.
A colleague recommended that I should re-engineer the system to use 75% recirculated air and only 25% fresh air, use one (or 4?) DX unit(s) to cool the air to 33 F, and then use SCR reheat for temperature control. I imagine I could install such units in place of the mixing boxes, and still utilize the existing ductwork. But I would have to find a way to draw room air (75%) into them.
Does this seem like the right approach? I would greatly appreciate any advice or suggestions you might be able to offer.
Thanks very much!!
Ben
I run a 1200 sq. ft. laser laboratory (12' ceilings). We would like to maintain the air in our lab at ~70 F, with a relative humidity less than about 35%. We have one fume hood in the room, which exhausts about 400 cfm. The remainder of the exhausting is performed by a single large duct leading to a rooftop fan.
Our supply air comes in through diffusers on four separate ducts running in our ceiling. These ducts originate from the hallway outside our lab, where there are four mixing boxes that mix the building hot & cold air. The building cold air is outside air that has been cooled to ~56 F, and the hot air is re-heated building cold air. This system provides good temperature stability (despite our variable heat loads from the lab equipment), but the humidity varies a lot and gets very high when it rains outside.
A colleague recommended that I should re-engineer the system to use 75% recirculated air and only 25% fresh air, use one (or 4?) DX unit(s) to cool the air to 33 F, and then use SCR reheat for temperature control. I imagine I could install such units in place of the mixing boxes, and still utilize the existing ductwork. But I would have to find a way to draw room air (75%) into them.
Does this seem like the right approach? I would greatly appreciate any advice or suggestions you might be able to offer.
Thanks very much!!
Ben