The maximum out of plane deflection, as per ACI318-08, shall not exceed L/150. And, ASCE recommends using the following load combinations for the purpose.
D+0.5L+0.7W
D+0.5L+0.7E
You can find these load combinations in Appendix C of ASCE 7-05.
Be sure to note that for slender wall design using ACI318-08, Section 14.8, service load deflection is to be calculated per Equation 14-8, by iteration of delections.