aun,
If I am understanding your post correctly, you have a precast pre-tensioned concrete girder bridge where the girder section is a U-section (or a trough section) with a deck slab that is composite with the girders. Several parallel girders will make up the full width of the bridge. span is 120 feet, girder depth is 54"?
A 2% deck cross-fall will have negligble effect on the composite section properties. You can include it simply enough but i would not worry.
For a precast pre-tensioned section you need to underake several calculations as non-composite and composite action. Presuming that the girders are self supporting across the span and do not have falsework or temporary shoring, then non-composite action shall be applicable up until the time that the deck slab has gained sufficient strength to be indeed composite with the precast section - e.g. camber and transfer calcs, weight of wet deck concrete, construction LL prior and during concrete placementetc. After the concrete deck gain strength then composite action is applicable and all future loads will be resisted via this action (ie the haunch effect of deck slab).
Bonded strands are those strands (pretensioned in this case) that are fully bonded to the concrete. Debonded (or "slipped" strands) strands are occasionally used to control stresses at transfer at the ends of the girder. Some DOT's do not permit debonded strands (increased corrosion is likely) so alternatively some of the strands can be harped (or "kinked"

at strategic location within the girder length to reduce the transfer stresses at the girder ends. A debonded strand has ZERO tension force (it is able to slip) at the locations where it is debonded. At other locations the stressed strands (most commonly 0.5" - 7 wire strand ) is stressed to 70% or 75% of UTS. But you need to account for prestress losses - both long term and short term - to arrive at the "effective prestress" force.
Are you familar with prestressed concrete design? For example, you need to undertake service stress calculations and do superposition of stresses for non-compsoite and composite actions, and you also need to check strength (flexural and shear) and also estimate deflections, and also longitudinal shear check etc.
HTH