With such a small load compared to the thermal-VA rating of a PT there might be some economy in a (local practices permitting) phase-to-ground-powered primary. In may areas, there are likely requirements for lamp-power reliability whenever a clearance beacon is mandated. PTs at poletops have been used for low-power SCADA remotes. Highside overcurrent protection for outdoor PTs is not customary in the US.
A PV install offhand seems like it could get pricey with a wide-temp battery set, charging control and PV array. It may be worth soliciting a quote, provided requirements are well understood.
I know of one attractive neon clearance beacon that is electrostatically powered by 230kV line proximity. Its cadence is a bit neurotic, so very unavoidable. I don’t know if it has required significant maintenance over the last ~25 years of operation. Accessibility looks a bit inconvenient, but it appears the power source has remained the same.