Suggestion to schweitzereaton (Electrical) Dec 17, 2003 marked ///\\Are there any benefits from grounding the neutral on a Y-D transformer? This is a small 750 KVA, 13.8KV to 2.3 KV. The secondary, 2300 volt side is ungrounded. The 13.8KV that supplies this transformer is grounded.
///It depends. How is system grounding upstream?
What is the transformer load in terms of the transformer availability and cost of the process or load downtime?
In some applications, the ungrounded power distribution systems are used since they can survive one fault to ground that is alarm only without any tripping. Also, any overvoltages caused by arcing may be suppressed and alarmed. This way the availability of the ungrounded power supply is high. This is usually referred to as a power supply for a dedicated load, or dedicated power supply.
If the above is not the case, then the grounding will limit overvoltage transients caused by arcing, cause positive trips of protective relays on fault conditions, break or modify the zero sequence current path, etc.\\