I guess you have never been to North America,
Demand billing is very common here.
Power factor penalties are very common here.
Commercial and industrial, anything over 120/240 Volts will probably be billed on kW, KVA demand, and with PF penaltis.
For a given motor, the PF will vary as the loading (kW) varies.
PF penalties are typically a percentage of the kW billing, so as well as being related to kW loading, PF penalties are related to kW charges.
I have worked in several plants where capacitors were used to over-correct the PF of the larger motors, and the leading VARs used to offset the PF of smaller motors.
It becomes very expensive to try to correct the PF of a large number of smaller motors.
Much more economical to over-correct a few large motors so that the overall PF is good.
PF control panels are becoming more and more common as the methods of calculating PF penalties become more sophisticated.
The bus or MCC to which the PF correction is connected will typically run at a leading PF.
You can't make assumptions about plant PF based on the PF of individual MCCs unless you have kW or KVA information to evaluate the overall plant PF.
What does kW have to do with PF?
Anecdote.
A small machine shop came to me asking if I could do anything about his PF penalty.
He had two quotes to correct the PF: $1000 and $2000. The second guy was hoping that he hadn't contacted the first guy.
He probably would have subbed the job out to the first guy.
Penalty on the bill looked bad, but how much?
The actual dollar value was almost insignificant.
I connected a motor running capacitor across one phase and that was enough VARs to correct the PF and get rid of the penalties.
Beware of knee jerk reactions until you have the whole picture.
By the way, that was a 100 Amp, 120/240 Volt delta service with demand and PF monitoring.
--------------------