Working on a project requiring very high motor efficiency. In reviewing motor selections, I notice with changes in the number of poles in asynchronous motors, PF changes. Can anyone explain why?
 
For the same horsepower, a lower-speed motor has bigger radius. That means larger rotor circumference. That means longer airgap (not deeper airgap... longer around the circumference).

Magnetizing a longer circumference to the same flux density will require more magnetizing amperes.

=====================================
Eng-tips forums: The best place on the web for engineering discussions.
 
Low pf in low speed machines is due to more flux leakages between the poles.
 
In my opinion both gentlemen are right. The rotor diameter is bigger if the poles number is bigger [as electricpete stated] .But as the magnetic flux will be almost the same (depending more or less upon the voltage), the magnetic flux density - measured in Gauss [or Wb/sqr.m=Tesla] will be different.
The rotor diameter will increase with the factor depending on p^ (2/3) that means for p=2 [4 poles] will be 2^ (2/3) =
1.587 times the diameter of 2 poles motor [roughly]. But the magnetic flux density will increase 2 time [as the air gap length per poles will be 1/2].So, ultimately, the flux density will increase 2/1.578= 1.267 times [roughly, of course!].
That means the saturation of the magnetic core [mainly in the teeth region]will be more pronounced in return, so the magnetizing amperes will increase[ as electricpete said].But in the same time also the notch leakage reactance will increase[ as edison123 said].The influence of the magnetizing current on the pf is evidently more important than the leakage reactance.
Best Regards

 
Tell us about your application. Induction motors are inharently inefficient since power is required to flux the rotor.
 
GREAT answers all - thanks! I'll try to stay of the EE's hair on this one! :)
 