Hi,
I have a capacitors installed in the low voltage side of a 750 kVA transformer (12.5 kV/208-120 V). The utility meter is on the high voltage side of the transformer and the monthly average power factor on the bill is under the penalty limit of 0.9. Therefore I made some measurements with a Fluke 1735 to see the power factor over the day.
The data showed that during working hours the reactive power is positive and the total power factor is always between 0.95 and 0.99, but at night and in the early morning the total reactive power is negative and the total power factor is below 0.9. When I compare the total power factor of the measurments with the one I calculete with the active and reactive power, there is a big difference. Here are some value:
PF Total kW Total kVar Total PF Calculated
0.893 14.25 -4.65 0.950
0.89 13.65 -4.8 0.943
0.897 13.56 -4.47 0.949
0.894 14.34 -4.44 0.955
0.885 13.26 -4.83 0.939
I thought that since the reactive power was low during the working hours and negative during idle hours, then my monthly average power factor in the bill would be over 0.9, but it's around 0.88. Another factor I realized was that the maximum demand was only 220 kW and the transformer is 750 kVA, so it's underutilized.
Some people have told me that I should change the tap in the transformer so it would reduce the reactive power it´s using since the capacitors aren't compensating the reactive power of the trafo.
Regards.
I have a capacitors installed in the low voltage side of a 750 kVA transformer (12.5 kV/208-120 V). The utility meter is on the high voltage side of the transformer and the monthly average power factor on the bill is under the penalty limit of 0.9. Therefore I made some measurements with a Fluke 1735 to see the power factor over the day.
The data showed that during working hours the reactive power is positive and the total power factor is always between 0.95 and 0.99, but at night and in the early morning the total reactive power is negative and the total power factor is below 0.9. When I compare the total power factor of the measurments with the one I calculete with the active and reactive power, there is a big difference. Here are some value:
PF Total kW Total kVar Total PF Calculated
0.893 14.25 -4.65 0.950
0.89 13.65 -4.8 0.943
0.897 13.56 -4.47 0.949
0.894 14.34 -4.44 0.955
0.885 13.26 -4.83 0.939
I thought that since the reactive power was low during the working hours and negative during idle hours, then my monthly average power factor in the bill would be over 0.9, but it's around 0.88. Another factor I realized was that the maximum demand was only 220 kW and the transformer is 750 kVA, so it's underutilized.
Some people have told me that I should change the tap in the transformer so it would reduce the reactive power it´s using since the capacitors aren't compensating the reactive power of the trafo.
Regards.