I have a problem.
We have an unbalanced 3 phase load from 2 distribution boards fed from a 60kVa ups.
Does anyone know of the equation for working out kVa of an unbalanced load from the 3 different line currents. The voltage is 415v (U.K.)
if your 3-phase load is not ballanced and not grounded, you will need to know the impedances of each phase, and all 3 currents. if your load has a ground (3-phase, 4 -wire), sum up the currents and multiply by 415V. What is your load?
For kVA, simply multiply each phase current by the appropriate phase voltage(L-N, or L-L Voltage/1.73) and sum. For circuits with similar PF values, this will be reasonably accurate.