I am investigating a 30 year old cast in place concrete mall parking structure in PA with grade level and roof top parking. The roof slab is 5 inches thick, reinforced with half inch diameter 270 ksi unbonded tendons at 3 feet on center with a parabolic draped profile. The typical slab span is 18 feet with some 23 foot spans over roadways below. The spans are continuous over PT beams spanning 63 feet with a 12" by 36" overall size.
Several spans appear to be sagging as much as 1 to 2 inches as measured with a string-line from beam to beam. (It is apparent to me that severe snow loads and related snow removal operations have taken their toll over the years. Soffit cracking is not widespread nor severe at this time.) Is their a way to analytically determine what I believe is a reduced live load carrying capacity, at the present time, based on center of span negative camber measurements or will some kind of physical load testing be required with strain gauges etc.?
Several spans appear to be sagging as much as 1 to 2 inches as measured with a string-line from beam to beam. (It is apparent to me that severe snow loads and related snow removal operations have taken their toll over the years. Soffit cracking is not widespread nor severe at this time.) Is their a way to analytically determine what I believe is a reduced live load carrying capacity, at the present time, based on center of span negative camber measurements or will some kind of physical load testing be required with strain gauges etc.?