I am checking an existing 30-year old post-tensioned 2-way flat slab with drop panels. The tendons are distributed about 60% in the column strips and about 40% in the middle strips (there is also some rebar that contributes about 20% to the moment of resistance; the negative top rebar is also distributed about 60% in the column strip). This does not conform to the 80% requirement for negative moment in the column strip, required by CSA A23.3 for 2-way slabs designed by the equivalent frame method.
Question: does the 80%/20% distribution of moment and reinforcent apply to prestressed concrete, or only to non-prestressed concrete?