Portal frame with hold-downs in engineered building?

Status
Not open for further replies.

AaronMcD

Structural
Aug 20, 2010
273
I was just perusing the California Building Code and discovered the existence of portal frames with hold-downs. I guess they can be use in typical non-engineered light frame construction, but I can't find any use of them in engineered construction (except for some random calc package I found through google). Would they be permitted? Would they behave? If so, what would be the appropriate response modification coefficient?
 
Replies continue below

Recommended for you

The APA portal frame is a tested and rated assembly that should be permitted for seismic design. Here's a report from the APA:


From the report: "For seismic design, APA recommends using the design coefficients and factors for light-frame (wood) walls sheathed with wood structural panels rated for shear resistance (Item 15 of Table 12.2-1 of ASCE 7-10). See APA Report T2004-59 for more details."
 
Thanks! I saw that report, but somehow missed the seismic coefficients (yeah I obviously didn't fully read it before posting here). The system isn't mentioned in ASCE 7, and the APA report isn't referenced by the code as far as I know so I still wonder if it would be permitted in high seismic areas. Any idea what the "load factor" column in the table is for? Or am I missing somewhere it explains this?
 