Thank you all.
Here is what I found in “GEOTECHNICAL ENGINEERING CIRCULAR (GEC) No. 8 - DESIGN AND CONSTRUCTION OF CONTINUOUS FLIGHT AUGER PILES – FINAL - April 2007” by FHWA.
7.5.1 Use of Integrity Testing
Integrity test methods require careful interpretation, which should be performed by experienced
personnel. However, integrity testing personnel cannot always determine whether an anomalous
reading is a defect within the pile; therefore, the final decision on acceptability of the pile must
be made by the design engineer based on the site specific soil conditions, construction records,
the post-installation integrity testing report, and analysis of the possible effect on foundation
performance.
As discussed previously, the most reliable means of achieving consistent QA/QC is automated
monitoring and control during construction, with documentation of the installation via these
measurements. The use of post-construction integrity testing is best utilized to verify that the
installation parameters used for control (i.e., penetration speed, grout or concrete pressures and
volumes during auger withdrawal) are appropriate for the site-specific project conditions.
Integrity tests can also be used to further evaluate piles that did not meet drilling or grouting
criteria. Coring of the piles can be used to supplement or to provide a visual check of suspected
defects detected by integrity testing.
[highlight #FCE94F]The necessary frequency of post-construction integrity testing is left to the judgment of the
owner and can vary from project to project. A frequency of 10% to 20% of production piles
subjected to integrity testing is typical. In addition, all preproduction and verification test piles
should be tested. When agencies have little experience with CFA piles, particularly difficult
project conditions exist, or project or site conditions give reason to expect problems with pile
integrity, integrity testing of more than 20% of production piles may be required. A typical
reasonable approach for load-bearing piles is to subject the first 10 to 15 piles to be constructed
on a project to integrity tests to establish that the contractor’s construction practice at the site is
adequate. Thereafter, the frequency of such tests can be set to meet the specified frequency
criteria, can be reduced, or even perhaps eliminate further integrity tests if the construction
records for the remaining production piles are similar to those of the initial piles that were
subjected to integrity tests.[/highlight]