pit design question (civil)
STEVE LIU
TW
hi~~
U = 1.4(D + F)...............(1)
U = 1.2(D + F + T)+1.6(L + H)+0.5(Lr或S或(2)
U = 1.2D + 1.6(Lr或s或R)+(1.0L或0.8W)...(3)
U = 1.2D + 1.6W + 1.0L + 0.5(Lr或S或R).........(4)
U = 1.2D + 1.2F + 1.0E + 1.6H + 1.0L + 0.2S ............(5 )
U = 0.9D + 1.2F + 1.6W + 1.6H ......................(6)
U = 0.9D + 1.2F + 1.0E + 1.6h.......................(7)
I design a pit now, and i dont need to consider wind load and earthquake at this area
if i consider combination 6 &7 and have not water inside pit
U = 0.9D + 1.2F + 1.0E + 1.6H.......................(7)
F=0, w=0, E=0 0.9D+1.6H H including groudwater, this combination make uplift load too large (1.6 multi)
let my analysis model error (compression only spring have tension)
actually uplift check is ok , consider this combination reasonable ?
Sketch your problem geometry and and label the dimension letters (to scale).
Your question is not clear enough to answer properly.
Depth, Width, Height (?), Floor (?), Uplift (?), Length (?), E ??,
I have a similar situation going on right now. I'm using the ASD load case .6D+H
Uplift is large with buoyant forces - displaced water = 62.4 pcf and weight of concrete = 150 pcf X .6 = 90 pcf.
Net gain of only 27.6 pcf.
Hi~~~racookpe1978 & hawkaz
thank for your replied
Sorry my roughly describe and i cant upload sketch right now i will do it later.
my pit almost 60 m x 60 m depth 5.5 m (underground)(bottom of baseplate)
wall thickness (0.6 m) baseplate thickness (1 m)
and water level at -3.6m so pit be submerged in groundwater 1.9 m.
My Situation like hawkaz
when i did buoyancy check without any load factor
only concrete weight / uplift force >1.2 ok ( almost 1.2).
But during finite element analysis ,
i consider the case of backfill with groundwater but without internal liquid
F=0 , w=0, E=0
U=0.9D +1.6H
this combination make uplift force too large.
so i think that i dont consider wind load and earthquake
i still need to consider these two combination or i can ignore it