Just looking for input, I have an engineer telling me of some piping voodoo 
We have a higher then normal pressure drop thru an 8" condenser line. calc = 10ft drop while actual drop is 18ft.
One engineer states that due to some tight transitions (ie: close coupled 90 deg elbows that the CV for each fitting in not valid and you cant get an accurate cv for close coupled fittings..... ????
another engineer thinks there may be a blockage in the pipe
at multiple points, as we took readings at many locations down the riser, and found 2 locations with higher loss's