Cut & pasted below is from the International Pipeline Contractors Association recommended practices for "Construction of Welded Steel Cross Country Pipelines", Volume 2, Part 1, Section 13, Hydrostatic Testing:
13.4 TEST EQUIPMENT AND FACILITIES
The Contractor shall provide all testing equipment including a mobile test cabin, filling and pressurising pumps, compressors, test end manifolds, pipeline pigs, instrumentation and recorders and all equipment and materials which may be necessary for water treatment such as
strainers, settling tanks, chemical dosing pumps, corrosion inhibitors and other chemicals.
Test end manifolds shall incorporate end closure and bypass valves and piping to enable cleaning and gauging pigs to be launched and received in a continuous series. A pig alert shall be fitted on the receiving end. Test end manifolds and other test pipe and fittings shall be designed for an internal design pressure equal to the test pressure and a design factor of 0.72. All welds shall be subject to
radiography and such other NDT as may be required to prove the integrity of the welds. Manifolds and other assemblies shall themselves be pressure tested at 1.25 times the pipeline test pressure.
Prior to each re-use, test ends shall be cut back to remove all weld metal and the heat affected zone. Test end manifolds and other assemblies shall be inspected prior to each re-use. Suspected damage shall be subject to such further inspection and testing as considered necessary.
Flexible hoses shall be armoured and shall have a safe working pressure at least equal to the test pressure of the test end manifolds. They shall be used only in short lengths for connecting to the test end and for instrumentation and the size shall not exceed ~“ nominal diameter.
13.8 TEST SECTIONS
Test sections shall be as long as practicable. Test lengths and locations of test points shall be set out in the Test Schedule and shall take account of the location of suitable water supplies and disposal facilities and allowable elevation difference.
On sections with significant elevation change the preferred test point and equipment location is at the section end having the lower elevation.
Adjacent test sections shall be constructed so that they overlap, and can be joined by a single tiein weld.
13.10 INTERNAL CLEANING AND GAUGING
Prior to testing, a single swabbing pig shall be driven through the section to be tested. This shall be followed by successive swabbing pigs until any water and debris have been cleared and the cleanliness of the section established.
Cleaning pigs shall be driven by compressed air and received in a suitable trap.
After cleaning, an approved gauging pig shall be driven through the test section. The gauging plate shall be aluminium, with a diameter of 95% of the minimum linepipe internal diameter. It shall be inspected before insertion and after passing through the test section. If any deformation or damage is unacceptable, or if the gauging pig becomes stuck, the Contractor shall determine the
cause and rectify it. The gauging pig shall be re-run if necessary.
Removal of pigs shall not commence until the pressure has fallen to atmospheric. Pigs should preferably be trackable.
13.11 WATER FILLING
After cleaning, the receiving test end manifold shall be welded to the test sections. (Where permanent launchers or receivers have already been installed, they may be used for filling and testing).
The test section shall then be filled with water. At least two swabbing pigs shall be used __ during filling. Washwater shall precede the first pig and shall be injected between pigs. The pigs shall be the correct fit, with new rubbers, and shall be separated in their travel to ensure that test water does not become aerated. The Contractor shall ensure that no air is drawn into the filling pump
suction. All fill pumps shall be fitted with 50 mesh suction filters.
On downhill sections the backpressure shall be adjusted to prevent runaway of the pigs. After all water-filling pigs have been received, water shall be flushed through the test section.
13.17 WATER REMOVAL AND DISPOSAL
Requirements with regard to water removal and disposal for a specific project should be addressed in the Particular Specifications. However the following general requirements shall apply. Uninhibited test water shall not remain in the pipeline for more than two weeks.
Before emptying a test section, the pressure shall be reduced to the hydrostatic head at the test point.
Wherever possible water from a test section shall be transferred into the next section. Water shall be
displaced using a minimum of two dewatering pigs. Water shall not be transferred directly to the next
pipeline section, any transfer shall carried out using a break tank Water disposal arrangements shall be set out in the Test Schedule and shall meet the requirements
of the relevant authorities. Particular attention shall be paid to the safe disposal of water, which has
been treated with inhibitors, bactericide or other chemicals.
Prior to transfer of water into adjacent sections of the pipeline, the new test section shall be cleaned in
accordance with Clause 13.10. Interconnecting pipework and test end manifolds shall be bled of air before filling commences. Filling and gauging of the new test section shall be in accordance with Clause 13.11. If test end manifolds of tested and emptied sections are cut off without immediate tie-in to adjacent sections, the pipe ends shall be sealed with secure end closures.