Below is my comments
>>As I said in the rest of my post, vertical loads are not the only consideration in a pipe rack beam.
I didn’t say the vertical load is the main concern. The piperack transverse moment frame’s moment can be caused by vertical gravity load, it can also be caused by the lateral wind or seismic load. It’s the combined of both gravity load and lateral load to get the final beam end moment.
>>In a rack servicing a large number of small diameter process pipes and cable trays you're going to see something >>trending closer to pure vertical loads
“pure vertical load” is not the case, lateral load cause beam end moment as well.
>>end up assuming horizontal loads of 30 or 40 percent of the weight due to friction against pipe expansion.
>>There are significant downsides to having a deep, thin beam when you're looking at a case with top flange weak >>axis bending.
That’s true but what we are talking about is the moment connection of TRANSVERSE moment frame, that friction load goes to LONGITUDINAL direction and it will go to strut beams and vertical braces.
Please note the deeper transverse beam is never intended to resist lateral load like pipe friction or anchor load. When there is big pipes and causing big pipe friction or anchor load, we use horizontal braces to handle that.
>> I wasn't disagreeing that use of a deeper beam can be a good solution. I was pointing out that it isn't necessarily >>the right solution for pipe racks seeing large horizontal loads because additional beam depth is generally a
>> negative in those cases and it causes other detailing and sizing problems.
Use of deeper beam is aimed to avoid the use of stiffener plate or doubler plate in the transverse moment frame’s moment connection. The use of deeper beam will not cause any negative to effect to the lateral load in the longitudinal direction. For large lateral load caused by pipe friction or anchor load, we never expect the open wide flange section can handle the torsion plus weak axis bending, in this case we use horizontal brace to brace out the lateral load to strut beam, to vertical brace, to foundation.
anchor bolt design per ACI 318-11 crane beam design