controlnovice
Electrical
- Jul 28, 2004
- 976
We have a powder transfer system: blowers, diverter valves, piping with large radius bends, to transfer powder from one silo to another.
Piping is aluminum (not sure exact spec), about 4" diam.
At the connection where two pipes are joined, the plant has installed a short cable, external to the pipe, from one pipe to the other, connected with a 'tab' welded to each pipe. This is to dissipate any static buildup during the transfer of material.
Every year or so, each of these 'bonds' are tested using a standard Fluke 87 for resistance. The probes of the Fluke 87 are pressed against the side of each pipe.
Is this a good test to verify the bond between the two pipes? I didn't think the 87 would produce enough voltage to give a good reading...and that a milliohmeter would be better.
I've also used a clamp-on ground tester to test grounds. Could this tool be used to test the bond cable?
______________________________________________________________________________
This is normally the space where people post something insightful.
Piping is aluminum (not sure exact spec), about 4" diam.
At the connection where two pipes are joined, the plant has installed a short cable, external to the pipe, from one pipe to the other, connected with a 'tab' welded to each pipe. This is to dissipate any static buildup during the transfer of material.
Every year or so, each of these 'bonds' are tested using a standard Fluke 87 for resistance. The probes of the Fluke 87 are pressed against the side of each pipe.
Is this a good test to verify the bond between the two pipes? I didn't think the 87 would produce enough voltage to give a good reading...and that a milliohmeter would be better.
I've also used a clamp-on ground tester to test grounds. Could this tool be used to test the bond cable?
______________________________________________________________________________
This is normally the space where people post something insightful.