A client (large Eng. company) asked me to review a single-span pipe bridge design, span >100ft. In the initial review (3 weeks ago) we introduced the subject of bridge camber, and had extensive discussions about weight, erection, galvanizing etc.
In the second round it became clear the design team is proposing the bridge be fixed at the towers, i.e. extended over both supports with bottom chords anchored front and rear. The bridge will project some 15ft over each tower, so the front-rear support spacing at each end of the span would be about 15ft. So we discussed negative bending in the bridge, the reaction-couple on each truss, the fact the front-reaction will be increased by the magnitude of the the rear/negative reaction, and how the towers will transfer the loads to foundations.
The client's design is taking advantage of reduced overall truss moments. They propose to include sliding connections at one end, in which slotted bolt holes allow sliding but can also provide the negative reaction force to tower.
To me this seems more complex and risky, than the simple-span approach. I've counseled thorough attention to detailing at the towers, to ensure all loads are addressed. I am accustomed to industrial bridges with simply-supported spans, and would naturally have used pin-connections, with expansion accommodated at one support by either sliding bearings or a doubly-pinned bent (or hanger).
The client has modeled the bridge and towers as one structure. My approach would require separate models, and there seems to be some resistance to the idea of back-pedaling.
We are also discussing lateral wind transfer from the top horizontal frame, as this force has to find its way thru the same set of connections, and we are discussing the possibility of a simple-span condition during erection. I should add, the foundations are very substantial and likely can take the negative moment.
Has anyone here used rigid/fixed connections for a single-span bridge (for pipes, conveyor, etc.)? Successfully? I really appreciate your thoughts.
In the second round it became clear the design team is proposing the bridge be fixed at the towers, i.e. extended over both supports with bottom chords anchored front and rear. The bridge will project some 15ft over each tower, so the front-rear support spacing at each end of the span would be about 15ft. So we discussed negative bending in the bridge, the reaction-couple on each truss, the fact the front-reaction will be increased by the magnitude of the the rear/negative reaction, and how the towers will transfer the loads to foundations.
The client's design is taking advantage of reduced overall truss moments. They propose to include sliding connections at one end, in which slotted bolt holes allow sliding but can also provide the negative reaction force to tower.
To me this seems more complex and risky, than the simple-span approach. I've counseled thorough attention to detailing at the towers, to ensure all loads are addressed. I am accustomed to industrial bridges with simply-supported spans, and would naturally have used pin-connections, with expansion accommodated at one support by either sliding bearings or a doubly-pinned bent (or hanger).
The client has modeled the bridge and towers as one structure. My approach would require separate models, and there seems to be some resistance to the idea of back-pedaling.
We are also discussing lateral wind transfer from the top horizontal frame, as this force has to find its way thru the same set of connections, and we are discussing the possibility of a simple-span condition during erection. I should add, the foundations are very substantial and likely can take the negative moment.
Has anyone here used rigid/fixed connections for a single-span bridge (for pipes, conveyor, etc.)? Successfully? I really appreciate your thoughts.