Structural
Dec 11, 2009
47
I am trying to find out the requirement for tie beams between pile caps in IBC 2009. Can someone locate the section reference please?

I remember from the old codes there was a 10% design value for the tie beams.

Thanks.
 
Replies continue below

Recommended for you

Grade beams (tiebeams) are discussed in 1810.3.11 & 1810.3.12 in 2009 IBC. There was no mention of the 10% design value. 1810.2.2 discusses stability requirments for pilecaps.
I usually design the GB (stabilizing 1PC & 2PC) for the moment and shear due to piles being out of tolerance
 
There is a 0.1 Sds multiplier on the seismic side on piles if that is what you are trying to refer to

 
Who cares? Ten percent of what, and what does it all mean? Forget about it. It has no meaning.

BA
 
I would perform a Strut and Tie model for the pile caps.
 
casasf,
The 10% times Sds that slickdeals referred to in his reply is found in section 12.13.5.2 in ASCE 7-05.
 
I hate it when people eagerly try to respond to a thread to help a fellow engineer and he/she disappears and we keep guessing as to what his question really is.

 
slickdeals,

I understand what you mean, but if you look at the record, casasf has started three threads to date and has made only one response. Does that tell you something?