Pilaster minimum reinforcement

tmalik3156

Structural
Joined
Jun 21, 2021
Messages
110
Location
CA
Good day all.
Sketch below is a pilaster of a wall. It's cross section is made of a steel section, and a reinforced concrete cover (C-shaped). The void where the steel is placed is grouted so that there is a composite action between the steel and the concrete.

A pilaster does not carry any significant vertical load, so it's not treated as a column. But it carries a significant horizontal wind load. The steel section is designed to carry that horizontal force alone. However, composite action reduces the horizontal deflection, so the concrete can not be treated merely as a cover.

What minimum reinforcement (shown in green) should we place in the concrete cover? Some people say just use 0.2% for temperature and shrinkage. But I think 0.2% is for slabs, not for a pilaster.

Thank you for your comments / suggestions.

Pilaster.png
 
For concrete columns you can go as low as 0.005 * Ag (in accordance with CSA) provided you reduce your Mr and Pr accordingly. Since the Mr is largely from the steel, you might be able to do this here.
 
I don't agree with the composite assumption. Composite action relies on vertical shear transfer between the steel and concrete interface...this is slick and there will be very little friction. You need welded studs or similar to be making that assumption.


I would be placing 4/ 10 or 12mm bars (1 each corner) and stirruping at say 300-400crs to provide a basic level of confinement
This isn't really based on numbers - just what feels right to me
 