- Aug 4, 2004
- 3
Hi All,
I was just wondering whats the best way to ensure phasing is correct between two sources, one is the ultility and the other is a emergency generator. Source voltages are 4160v and has two sets of PTs connected Open Delta with B-phase grounded on each. I was thinking of doing a rotation check on both sources and compare them. I am also going to do a phase angle check with phase B- as reference, what angles should I be seeing?
Thanks any help would be appreaciated.
Golruss
I was just wondering whats the best way to ensure phasing is correct between two sources, one is the ultility and the other is a emergency generator. Source voltages are 4160v and has two sets of PTs connected Open Delta with B-phase grounded on each. I was thinking of doing a rotation check on both sources and compare them. I am also going to do a phase angle check with phase B- as reference, what angles should I be seeing?
Thanks any help would be appreaciated.
Golruss