7.2 Locked-rotor tests
7.2.1 Current
This test may be performed either to check for quality or to determine performance. When possible, readings
shall be taken at rated voltage and frequency since the current is not directly proportional to the voltage
because of changes in reactance caused by saturation of the leakage paths. When the test is made to check
the quality of squirrel-cage machines, it is possible to omit the mechanical means of locking the rotor by
applying single-phase power of rated voltage and frequency to any two of the machine line terminals of a
three-phase machine. With a three-phase machine, the line current will be approximately 86% and the power
input will be approximately 50% of the corresponding values obtained with polyphase power. The values so
obtained may be compared with those measured on a duplicate unit that has been subjected to a complete
test.