Okay folks, I'm looking for your thoughts on this one.

Related thread:
I have a single slope PEMB frame that experienced extreme snow load this past winter. Both columns bear on a 10" wall extending 48" about the floor (we all know that's not smart, so don't go there). No pilaster under the columns, only 2 out of the 4 anchor bolts were installed. I would bet there's no reinforcing in the wall. The horizontal load at the base of the taller column cracked the 3'-3" wide, 10" thick wall at the floor line and temporarily pushed it out about 2". This wall is between 2 overhead doors. After the roof was cleared and the the weather warmed up, the wall almost returned to its original position.

My question for those with more experience with PEMBs than me: Analysis shows that if the bottom of either column is allowed to move in the horizontal direction, the maximum positive moment in the roof beam increases to about 140% of the fixed column base condition. What kind of weakening of this frame could have occurred? There was no collapse, just damage to the foundation wall at one end.

I will be examining all bolted connections this week (haven't done so yet because of the height) to look for distortions around the bolt holes. I have also posed the same question to the PEMB manufacturer. This has been lingering while we wait for the owner's insurance company to determine what they want to cover. I am advocating rebuilding the wall and foundation at each end of the frame to accommodate all design forces applied by the columns. I sense that the insurance company only wants to cover the failed wall and nothing else.

I will save the editorial comments about residential foundation contractors (who built the foundation) and semi-retired builder inspectors (who asked for a foundation design by a P.E. but didn't follow through).


Ralph
Structures Consulting
Northeast USA
 
Replies continue below

Recommended for you

guess I'm dull or something with the quotes, but I typed it in and it didn't work. Got it now. Sorry everyone.

then it'd be in your
 

a2mfk: Sorry, I forgot to respond to your question - I'm representing the building & business owner's interests. The adjuster who visited the site recommended that they cover the loss. It's the inside adjuster who's balking at covering all of the repairs that I feel are appropriate.

From my perspective, it's simply a case of pay now for reasonable repair costs (estimated to be about $30K), or pay later when the entire 2-bay addition hits the ground and crushes all of the owner's equipment inside.

Ralph
Structures Consulting
Northeast USA
 
Ralph,
Here's a link.....leave your contact info in the general contact...

WEI

 
WHOA! Small world Ron! Your coworker and I went to school together and were friends at FSU... Liked that guy a lot.
 
Is there an engineer for the insurance company?

They are usually pretty conservative with repairs too, and if you have to rebuild the wall and foundation to perform the repair, that has to be done to code, and they have to pay for it. Whether or not the original structure met code or standard practice, like I said, in my experience, is rarely an issue. The repair simply needs to be done.

Despite what most people think or their impression is, property insurance companies in my experience are very fair, conservative, and often pay above and beyond what I would think is required...
 
a2mfk...even smaller world...I'm as FSU for freshman orientation with my son! He's not going into engineering, though!
 
"as" should be "at"...sorry guys...can't type
 