On page 17 it states:
Question 1 - Does anyone have any opinions on this configuration or the quote above?
Question 2 - Do you know of guidelines for installation of coupling caps together with surge caps to ensure the surge cap does not interfere with the coupling cap function?
Just thinking through this. If the taps were separated by 0.5 meter... round trip distance is 1 meter.... at 3E8 m/sec the round trip takes 3 nanoseconds. Probably the rise times of interest are considerably longer than 3 nanosecond which suggests there would be interference in sensing of pulses from the motor at the coupling cap if spacing is 0.5 meter.
=====================================
(2B)+(2B)' ?
We have this exact configuraiton: 80 pF pd coupling (sensing) capacitors applied in the same term box as 0.25 uF surge caps, although the pd coupling caps tap in closer to the motor.Retrofitting or installation of surge capacitors with high frequency current transformers is the solution for sensitive pd measurements on generators and motors. Furthermore, if surge capacitors are already fitted it is useless to fit additional coupling capacitors as the surge capacitors drain their signal energy.
Question 1 - Does anyone have any opinions on this configuration or the quote above?
Question 2 - Do you know of guidelines for installation of coupling caps together with surge caps to ensure the surge cap does not interfere with the coupling cap function?
Just thinking through this. If the taps were separated by 0.5 meter... round trip distance is 1 meter.... at 3E8 m/sec the round trip takes 3 nanoseconds. Probably the rise times of interest are considerably longer than 3 nanosecond which suggests there would be interference in sensing of pulses from the motor at the coupling cap if spacing is 0.5 meter.
=====================================
(2B)+(2B)' ?