Please consider the following:
1. Existing E/G system is a random access, parallel, three E/G switchgear.
2. A 3000AF drawout power breaker on E/G switchgear is presently serving a 480Vac, 1200A load using 4/phase 600MCM Al conductors. The linear distance is approx. 1000ft.
3. A new 3000A, 3 phase, 4W Cu busduct feeder was installed to replace the Al conductor feeder.
4. A last minute decision was made to retain the exisiting Al feeder fed from the 3000AF breaker and conncect the Cu busduct to the same breaker using 600MCM Cu conductor. To do this 6 new Al/Cu lugs/phase will be added to the breaker output. Each feeder will be serving separate loads. The power breaker rating plug will be increased to 3000A.
Some of us feel that the busduct feeder should utilize a separate breaker. This will provide an opportunity for better coordination, diversity, selectivity, etc.
Opinions please.
1. Existing E/G system is a random access, parallel, three E/G switchgear.
2. A 3000AF drawout power breaker on E/G switchgear is presently serving a 480Vac, 1200A load using 4/phase 600MCM Al conductors. The linear distance is approx. 1000ft.
3. A new 3000A, 3 phase, 4W Cu busduct feeder was installed to replace the Al conductor feeder.
4. A last minute decision was made to retain the exisiting Al feeder fed from the 3000AF breaker and conncect the Cu busduct to the same breaker using 600MCM Cu conductor. To do this 6 new Al/Cu lugs/phase will be added to the breaker output. Each feeder will be serving separate loads. The power breaker rating plug will be increased to 3000A.
Some of us feel that the busduct feeder should utilize a separate breaker. This will provide an opportunity for better coordination, diversity, selectivity, etc.
Opinions please.