Three key consideration apply when determining whether a substation style transformer or pad-mounted transformer should be specified: location of transformer, location of incoming and outgoing cables, and loading.
Substation style transformers may be economical choice when:
1. public access to the transformer is not a concern
2. incoming cables are overhead, or transformer is close-coupled to separate switchgear
3. additional flexibility to handle overload conditions is required.
In addition, substation style transformers allow you to view the gauges, purge gas, and take oil samples without having to open the transformer cable termination compartments.
Pad-mounts are typically used where tamper-proof enclosures are required due to public access. All the gauges and accessories are located inside the cable termination compartments. In addition they tend to be smaller than substation style and take up less space. They also tend to be more aesthetically pleasing.
"Throughout space there is energy. Is this energy static or kinetic! If static our hopes are in vain; if kinetic — and this we know it is, for certain — then it is a mere question of time when men will succeed in attaching their machinery to the very wheelwork of nature". – Nikola Tesla