Procman:
Both saxon & jay165 have hit the nail on the head. The strongest, most logical and forceful reason that you have to eliminate the scroll-type of P&ID is that this type of drawing is not subject to change easily in a timely and cost-effective manner.
If your plant is within the USA, you are subject to OSHA mandates and legal requirements and, as such, must maintain your P&IDs up-to-date (on a day-to-day basis) with every change, addition, or removal of equipment that takes place. This is in keeping with OSHA's PSM policy and follows their dictates on Management Of Change (MOCs - remember them?).
There was a time when the P&ID was an archival document: it was drawn and filed for reference and as a museum piece. This no longer is the case legally. The P&IDs are now regarded as living documents subject to modifications and changes, as per MOC, and must be kept at the ready for review and inspection by OSHA whenever they come a'calling at the front gate.
These legal requirements must be met and you will soon find that you must have the facility to add (& remove) sections or portions of your P&IDs. This is why the Sheet Method is the only way to go, and the "strip" method cannot function properly under such requirements.
If you can't convince your supervisors with the above information, they deserve the opportunity to pay the difference in maintaining the P&IDs.
Art Montemayor
Spring, TX