I read that thread, it really doesnot confirm the need of overflow slots or overflow protection on EFR tanks..
One of the post from "IFRs" says that he is designing tank from years and have not given overflow protection to tanks..
[highlight #F57900]IFRs (Petroleum) 1 Jan 08 15:02
FYI - the "vents" you see in the tank shell or fixed roof are for ventilation, per API 650 Appendix H. They serve to reduce fixed roof underside corrosion and keep the air/vapor mixture above the IFR below the LEL. The tank will be protected from pressure or vacuum as a by-product of the huge holes required for adequate ventilation (2 square feet per 10 feet of tank diameter). Many of the tanks that I design have no shell vents or overflow ports. You really won't hurt the floating roof that much by forcing it into the fixed roof rafters while a overfill (read "spill") costs so much more that any IFR damage is worth the extra protection of additional shell height. High, high-high and emergency alarms and shutoffs seen to do the trick. I have been designing, manufacturing, installing and repairing aluminum and steel IFRs since 1977 and designing tanks for nearly that long also[/highlight]
Also API 2350 and API 650 does not clearly adress the mechanical arrangement for overfill protection on EFR tanks...
Please guide..