Sorry, didn't mean to imply that ALL drives are incapable of over speed in Vector mode, only that this might be a possibility. It has to do with the power of the mP in the drive. SVC requires that the mP maintain a mathematical model of the motor that you either enter manually or it determines by "auto-tune" at setup. Then it has to compare what is sees in the motor current response to step changes against that model and against what you have told it to do in terms of performance (speed regulation, torque regulation etc. etc.). Once you go above base speed, it has to do a lot more number crunching because the motor torque is now diminishing. Cheaper drives don't have the intestinal fortitude to take that on, more expensive ones do, but even then only to a point. Usually there are separate output frequency limits based on the operating mode, i.e. 200Hz for SVC, 400Hz for V/Hz (took that from a Fuji drive spec as an example). If the drive makes no claims to such limits, it usually means they can handle anything you ask it to do, but even then I have been caught by a "gotcha" on that issue when I tried to run a Teco drive in SVC at 75Hz. No can do, but it made no mention of that, I had to hear it from their app engineer.
So I mentioned it as a probable cause in this case because it seems as though the OP is having that same kind of experience I had when that happened to me. I thought I had everything set correctly, and I did, but the drive just wouldn't do it, because as it turned out, it couldn't unless I put it into V/Hz mode.
Now that I've had time to look at the manual link, it appears as though this drive can handle up to 120Hz and makes no restrictions on V/Hz or SVC, so one would imply from that it is capable of it.
So ports394,
How are you giving it a speed command? From what I see, if you are using something other than the keypad or serial comms, you have to program the maximum speed that an external reference will allow, it doesn't seem to be one setting that universally applies regardless of the speed command source. So if for example you set BAS-07 to 70Hz (Maximum Frequency) but you are using an external speed pot or 0-10VDC signal, you have to purposefully set I/O-5 to 70Hz as well to allow the maximum voltage to equal the maximum frequency reference. If you didn't change that, the default is 60Hz. If it's a 4-20ma signal, you use I/O-10 to set the max. frequency for that reference signal.
"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)
For the best use of Eng-Tips, please click here -> faq731-376