Yep - Crown06 - just to repeat - when you design a joist, it has a theoretical shear capacity that varies across the span from the original max. end reaction - to 0 at midspan. However, the SJI requires the joist manufacturers to at least design the joist web members for 25% of the shear at the end (some years ago it was 50% so the older the joist the more hefty the webs).
When you shorten a joist span, you have the potential to create a larger shear at the new end from what it was originally designed for. Simply construct an "original" shear diagram and superimpose it over your new shear diagram to check if you are ok.