sparks22222
Electrical
- Jul 23, 2002
- 11
Hey guys,
I came across this VFD problem in one of our locations.This plant had a problem with an Omron VFD where the drive (5.5kw) is operating a rooftile holder which goes up and down at low and fast speeds with a brake installed.
Well before i came to the location(3 y old only) the electrician had changed the braking resistor which was heating up(which couldnt be touched)after a few runs of the drive.He changed this braking resistor(resistance was low) even changing a few of them but with all heating up.At that stage the inverter had overloaded and eventually shorted out on the L1/L2 input terminals.
Once the electrician had changed the inverter with the same type(OMRON)and this worked for a while but same problem showed up again and eventually burned out the second inverter as well.(Shorted out on L2/L3)
At this stage i came on the scene to face this problem of no inverter in stock.So we had a UNIDRIVE VFD for 7.5kw and tried this to get us out of a hole.So while we waited for the next OMRON inverter we decided to check why both inverters burned out.So we changed the 5.5kw brake (sew)motor(couldnt check resistance,no megger) and replaced the motor cable and then tried the UNIDRIVE inverter.After some time sorting out the parameters in the new inverter,we eventually got this drive running.
Just wondering has anyone come across this problem or something similar.Why was the braking resistor heating up (i know probably from too much regenerative energy being supplied from the motor when braking hard) and the inverters damaged and the strange thing is we dont know where the problem was after all this.It may have been the motor,the cable,the resistor(which i dont think)or the inverters.
I have come across some inverters where the dc bus is damaged and they are replaced by me but this was an odd one.
I appreciate any help on this.
I came across this VFD problem in one of our locations.This plant had a problem with an Omron VFD where the drive (5.5kw) is operating a rooftile holder which goes up and down at low and fast speeds with a brake installed.
Well before i came to the location(3 y old only) the electrician had changed the braking resistor which was heating up(which couldnt be touched)after a few runs of the drive.He changed this braking resistor(resistance was low) even changing a few of them but with all heating up.At that stage the inverter had overloaded and eventually shorted out on the L1/L2 input terminals.
Once the electrician had changed the inverter with the same type(OMRON)and this worked for a while but same problem showed up again and eventually burned out the second inverter as well.(Shorted out on L2/L3)
At this stage i came on the scene to face this problem of no inverter in stock.So we had a UNIDRIVE VFD for 7.5kw and tried this to get us out of a hole.So while we waited for the next OMRON inverter we decided to check why both inverters burned out.So we changed the 5.5kw brake (sew)motor(couldnt check resistance,no megger) and replaced the motor cable and then tried the UNIDRIVE inverter.After some time sorting out the parameters in the new inverter,we eventually got this drive running.
Just wondering has anyone come across this problem or something similar.Why was the braking resistor heating up (i know probably from too much regenerative energy being supplied from the motor when braking hard) and the inverters damaged and the strange thing is we dont know where the problem was after all this.It may have been the motor,the cable,the resistor(which i dont think)or the inverters.
I have come across some inverters where the dc bus is damaged and they are replaced by me but this was an odd one.
I appreciate any help on this.