I read the abstract for ANSI 12.12.01-2000. It appears to be details on designing components/equipment which will be certified for Class 1, Division 2. It doesn't say it covers installing these devices in a system.
As for the NEC, it sure reads like a legal document. I understand there's a panel involved, but I'd be shocked if there were lawyers on that panel.
Can somebody explain this to me?
"Nonincendive Field Wiring. Wiring that enters or leaves
an equipment enclosure and, under normal operating conditions
of the equipment, is not capable, due to arcing or
thermal effects, of igniting the flammable gas-air, vapor-
air, or dust-air mixture. Normal operation includes opening,
shorting, or grounding the field wiring."
That last sentence is the stumbling block. It sure sounds like a fault condition to me. Unless they are talking about a switch or other hazardous-are field device, but then they should have been more clear about it.
If you really want to strain your brain, try to decifer this. I had to read it about four times before I could even guess at it's meaning.
"Associated Nonincendive Field Wiring Apparatus. Apparatus
in which the circuits are not necessarily nonincendive
themselves but that affect the energy in nonincendive
field wiring circuits and are relied upon to maintain nonincendive
energy levels. Associated nonincendive
field wiring apparatus may be either of the following:
(1) Electrical apparatus that has an alternative type of protection
for use in the appropriate hazardous (classified)
location
(2) Electrical apparatus not so protected that shall not be
used in a hazardous (classified) location
FPN: Associated nonincendive field wiring apparatus has
designated associated nonincendive field wiring apparatus
connections for nonincendive field wiring apparatus and
may also have connections for other electrical apparatus."
Finally, I understand that the NEC is not intended to be a training document. If you are new to this, find someone who isn't. But much of the verbage that they have added to the 2002 code (vs the 1999 code) to "clarify" nonincendive installation seems to be intentionally vague, in my opinion.
-Brad