gd72:
The correct Nitrogen blanketing pressure to employ in your application is related to the characteristics of your system. I assume you are applying it to a fixed, cone roof, API 650 or API 620 design. It depends on:
1) The MAWP and MAWV (Max. Allowable Working Pressure & Max. Allow. Working Vacuum) of your tank;
2) The liquid fluid stored;
3) The type of Nitrogen instrumentation, level controls, and relief devices employed;
4) The location and maximum site temperature expected;
5) Whether you vent the excess N2 to atmosphere or recompress.
For example, the vapor pressure of THF is approximately as follows:
Temp, oF VP, mmHg
100 275
110 375
115 400
120 425
Obviously, if you’re in Phoenix, Arizona you can expect your tank to exhibit about 450 – 500 mmHg pressure around mid-day. You want to select a Nitrogen pressure above the THF vapor pressure that will ensure that you have a positive pressure in excess of the THF vapor pressure such that the tank vapor space is pressurized above the atmospheric pressure. This keeps out air and water vapor and keeps the volatile and flammable THF contained under a positive, inert pressure.
Your tank’s vapor space pressure will swing in accordance with the level of fill, the temperature, and whether it is being filled or emptied of THF. As you lower the THF level, the vapor space volume increases and its pressure decreases. This is where the N2 supply valve would normally open, at a pre-determined set point. You want to avoid having a varying liquid level if possible, because this causes a demand for N2 when the level drops and an excess of N2 (that must be vented or recovered) when the level is subsequently raised (thereby increasing the N2 vapor space pressure). This creates a need for a liberal “dead-band” – that tank vapor space pressure range within whose limits the instrumentation is set to operate. Depending on the sensitivity and accuracy of your instruments, you may have to increase the limits of the dead-band. This is why you must take into consideration the tank’s pressure and vacuum limits.
You have a need to design for the lowest tank vapor space pressure (which activates the opening of the N2 supply) as well as the highest vapor space pressure (which activates the tanks vent relief system or conservation vent). The ideal storage tank allows you to impose a slight N2 vapor space pressure when it is practically empty (around, say 5-10” W.C.) and withstands the resulting pressure reached when the tank is filled with THF to the maximum height (approximately 90% of total capacity). But normally what takes place is that you have a specific design on your tank that you must adhere to and those limits are what you design the N2 blanketing system to operate within.
I have produced and stored THF in the past and I remember that I employed a dead-band of 20” W.C. in my storage tanks. Unfortunately, I don’t recall the pressure ratings on the tanks and the specific sizes.
I presume you will be employing API 650 or 620 tank(s) with cone roofs and the tank(s) will be anchored to a concrete ring foundation. I also assume you will monitor (& record) the vapor space pressure to ensure blanketing and also to reveal when you vent. Tight environmental emissions controls and N2 costs may require you to do this monitoring.
I hope this explains how to go about picking your blanketing pressure design criteria.
Art Montemayor
Spring, TX