Hey All,

I am new to using Proface and I am looking for some good tutorials out there to help. I am using the GP-Pro EX V3.6 software and my hardware is an LT3300. Any suggestions?

Thanks,

Careve01
 
1. Try to stay away from scripting in Pro-face, its dog slow.
2. Do not directly link your symbol tags directly to a PLC tag, use an intermediate tag as given on left side of the symbol database. This is standard practice in a lot of HMI programs.
3. I thought the documentation had examples, but have never used them.
 