Need to set a pre loaded load cell value to zero in PLC.

Status
Not open for further replies.

vivekigles

Industrial
Aug 1, 2022
4
Screenshot_59_icjrxz.png


The data coming from a Load Cell U4/G102 is moved to D3200 (The load cell at home position has a pre-load applied of 6 KN). The data mmoved into D3200 from load cell, I want to make it Zero.

How can I do that?

Please help.
 
Replies continue below

Recommended for you

Subtract the pre-load from the value in the storage register D3200 on a rung immediately after the move command and before the value is used in any other places.

xnuke
"Live and act within the limit of your knowledge and keep expanding it to the limit of your life." Ayn Rand, Atlas Shrugged.