Need to set a pre loaded load cell value to zero in PLC.

Status
Not open for further replies.

vivekigles

Industrial
Joined
Aug 1, 2022
Messages
4
Location
IN
Screenshot_59_icjrxz.png


The data coming from a Load Cell U4/G102 is moved to D3200 (The load cell at home position has a pre-load applied of 6 KN). The data mmoved into D3200 from load cell, I want to make it Zero.

How can I do that?

Please help.
 
Subtract the pre-load from the value in the storage register D3200 on a rung immediately after the move command and before the value is used in any other places.