Existing steel beams framing into cast iron columns and brick piers. We will be substantially increasing the load so we will be adding new steel columns adjacent to the existing and completely discounting the cast iron columns. This means fitting a new steel post at each floor from top of existing beam to underside of existing beam and detailed to carry all load. What's the best way to detail this such that it's reasonable to build and I can still be assured of load transfer?
I am thinking to add vertical plates to the existing members that align with the faces of the new post and transfer the load through fillet welds of plate to new post. This would allow for tolerance such that the post doesn't have to exactly fit. Loads aren't huge, around 100kip at lowest floors.