MSUK90 said:
KootK, how do we achieve option 2b suggested by you at site?
It depends on a bunch of details of the new and existing construction that I'm not privy to but, similar to nivo_boss's suggestion, often this takes the form of rebar dowelling.
If your root concern is that it may well be impossible to tie the new and existing foundations together to transfer the full, factored, differential load that may occur between them then I quite agree. My detailed response to that would be:
1) Franky, such convincing interconnection is rarely even possible with lightly loaded foundations if one is honest with themselves about the realities of load eccentricity and anchorage design, often involving shear directed towards a free edge.
2) I have been assuming that the two buildings in question here will be part of a common facility with passageways connecting the two. Where that is
not true, I would rarely connect the new and existing foundations. Where that
is true, one of the more dire, practical concerns with differential settlement is differential floor movement at the interfaces between the two buildings. It is for this reason that I, and many before me, choose to create some manner of interconnection between new and existing structures even when transferring the full differential load from one side to the other is impossible. Often, the interconnection will help to prevent serviceability issues from arising during the service life of the structure. And, also often, the consequences of the interconnection failing are not not, themselves, any more dire than the development of the differential movement issues at the interfaces.
3) One of the primary purposes for installing grade beams in piled foundation systems is to help iron out differential settlement between the piles. For that purpose, we usually provide grade beams designed to transfer a very small share of the maximum pile load between piles. That, in acknowledgment that one doesn't necessarily need to transfer a huge proportion of the total load between piles in order to positively impact the differential settlement performance. I see the pile and grade beam business as being analogous -- albeit imperfectly so -- to the situation of new footings installed against adjacent footings.
MSUK90 said:
And wouldn't tying the new footing to the old one will overload the old footings?
Possibly, however:
4) With capable enough interconnection, the new and existing buildings will share their combined loads among their combined footings which, hopefully, yields a satisfactory result for both.
5) Out of necessity, foundation design usually winds up being an immensely pragmatic exercise. I find that, if I restrict myself to avoiding every possible, on paper issue, nothing gets done. So I choose to focus my efforts primarily on the things that I really and truly believe may cause real world future problems.
6) In a sense, the new footings may overload the existing footings even if the two are not interconnected. That, because the new and existing footings are likely to share a common stress field below their combined area. But, sure, some thought certainly ought to be given to the foundation construction above the soil interface and whether or not new loads imposed there may cause problems. That's the "engineering" part of the exercise after all.
7) For loads of this scale, I would insist on having the assistance of a geotechnical engineer on the project and would tailor my solutions to suit their recommendations.