rockman7892
- Apr 7, 2008
- 1,176
I'm involved in the early conceptual stage for a project that involves expansion of an industrial customer process which will add and additional 70MVA to their current base load of aprox 30MVA. In total new plant demand will be 100MVA.
The existing 30MVA base load is currently served by a utility service at 34.5kV but with the addition of the new 70MVA this will exceed 34.5kV capacity and utility will require plant to upgrade to 138kV service from nearby 138kV transmission lines.
I was hoping to get some input here from some folks on the utility side to hear standards, opinions, etc.. from utility perspective on this type of transmission service on a customer property.
1) My understanding with transmission level service is that due to NERC requirements the 138kv transmission service can be built on customer property but must be owned and operated by utility? Is there a typical voltage threshold at above which voltage these requirements come into play?
2) The customer's plant distribution will be 34.5kV so customer will build adjacent substation with 138kV-34.5kV transformers which they will own/operate. In this application with utility 138kV yard on-site is it typical for utility to leave their yard with breaker to feed over to nearby customer yard (one or multiple breakers depending on arrangement). What type of protection does the utility require that the customer provide on these incoming lines? In the case where customer has transformer in their yard does utility require customer to provdie high-side protection of this transformer (IE incoming breaker) in order to trip customer breaker before tripping off utility breaker?
3) Utility in this case requires customer to maintain a .95pf Lead/Lag however there is no documented PF penalty. Is that typical for utility to require high PF at this transmission voltage? Do they typically charge PF penalty if not met?
4) Does utility always require customer to pay for capital expense of any new service (distribution or transmission) with the cost of new equipment and construction? Is this always required for customer to pay up front, or does this sometimes can incorporated into rate charge?
5) The billing rate per kwh at 138kV is a fraction of what it is at 34.5kV. What is usually the typical driver for this much lower rate?