Hi Scotty.
I underastand at you as well.
It's not so simple change logic of interlocks , change philocophy of EE, but we must do it. We must change our mind. It's our future, substation w/o HW interlocks, only SW interlocks.
I don't want disscaus about advantages and disadvantages of IEC61850 ( I haven't any experience with this protocol).
But I have 10 years expirience with other protocols and commissioning at about 45 substations with peer to peer ( bay to bay )communication between IED. All SS with HW and SW intelocks in parallel. It's expensive, hard commissioning
and today ( after 10 years) I understand we don't need so much "redundancy". In additional IEC61850 open for us new option of redandancy:
1. ring connection.
2. double ring connection.
3. full monitoring of communication
etc, etc.
What is our problem, we need learn again.
I think, Scotty, your big problem on this moment and not only your, we depend on many communication "tricks".
But, I'm sure, after good courses, Scotty,you, with your background and experience, will understand, what you have and will happy.
No repeater relays, no wiring betweem bays, additional terminals , interconnection diagrams, etc.
So, as Iz5pl, saied, don't worry, but watch carefully comissioning. I would like add, request from vendor test:
1. Operation in several undefined position of elements.
2. Operation in case of problems with Rx and Tx separatly.
3. Loss of power supply of network switches, check recovery tiome of system.
4. Indication of loss of communication on bay controllers.
5. Overriding.
Second, you are not first.
And, we with you.
Iz5pl, O.K. you have now two ES (grounding switch) on both of ends of line. And don't have communication, no problem:
"No communication-no permit to close"' it's rule.
"No clear position of object-no permit to close"
Now, you have HW interlock, you don't know, what is a status of aux. contacts, what happend with control cable.
In case of FO, you have on-line monitoring. In case of SW interlocks, we work with double indication in case of HW interlocks it's only single.
Why, we don't say about "new" BBP, line differntial protection, it's work many years w/o problem and based on FO communication. What is a differnce?
Regards.
Slava.