Sep 16, 2020 #1 R Mohan Electrical Joined Sep 16, 2020 Messages 2 Location IN I want to know how to calculate the neutral grounding reactor size which is being used for grounding a shunt reactor of 400 kV transmission line. If any one know please let me know.
I want to know how to calculate the neutral grounding reactor size which is being used for grounding a shunt reactor of 400 kV transmission line. If any one know please let me know.
Sep 20, 2020 #2 7anoter4 Electrical Joined Oct 5, 2007 Messages 2,907 Location IL See-for instance: https://na.eventscloud.com/file_uploads/1ab4d67dd86dae934ff4ed4f96e79400_fis2_pap.pdf Upvote 0 Downvote
See-for instance: https://na.eventscloud.com/file_uploads/1ab4d67dd86dae934ff4ed4f96e79400_fis2_pap.pdf
Sep 21, 2020 #3 7anoter4 Electrical Joined Oct 5, 2007 Messages 2,907 Location IL See attached a calculation example. https://files.engineering.com/getfile.aspx?folder=a373840f-e95b-416d-be32-0c7175f42f8d&file=Shunt_Reactor_Grounding.jpg Upvote 0 Downvote
Sep 24, 2020 Thread starter #4 R Mohan Electrical Joined Sep 16, 2020 Messages 2 Location IN Dear 7anoter4, I have the same pdf mentioned by you. The sample calculation shared by you has cleared my doubts. Thanks for the reference. Upvote 0 Downvote
Dear 7anoter4, I have the same pdf mentioned by you. The sample calculation shared by you has cleared my doubts. Thanks for the reference.