Think of this the same way as a vector being resolved into components on the x, y, and z axes. The components exist to describe pieces of the actual vector. They are a mathematical change of representation to make difficult math easier to solve by looking at the components independently. The math we apply is known as a transform.
We also do a change of representation, i.e., apply a transform, to make the difficult math of unbalanced three-phase system analysis easier to solve by breaking the unbalanced phasors down into balanced components which we can then look at independently. Three-phase unbalanced current phasors can be resolved into three balanced component three-phase phasor sets on three different "axes": positive sequence, negative sequence, and zero sequence. These can be known as the ZPN domain. The phasor component axes in this domain are defined as all rotating in the same direction - counterclockwise. The positive sequence axis is defined as having phasors of equal magnitude separated by 120 degrees with the same phase sequence as the total current (ABC), the negative sequence axis is defined as having phasors of equal magnitude separated by 120 degrees with the opposite phase sequence (ACB, hence opposite phase sequence to the rotor rotation which is in the ABC direction), and the zero sequence axis is defined as having phasors of equal magnitude separated by 0 degrees.
When you calculate the NPS, you are calculating the projection of the unbalanced three-phase current onto the negative sequence "axis," much like you can calculate the projection of a vector in the xy plane onto the x-axis to determine its component along that axis. The negative sequence current does not exist independently, it is just a component of it.
Are the sequence components real? That begs the question of causality. Is it a vector that causes its components, or do the components cause the vector? I prefer to think of it the first way, though just for my peace of mind because I know that causality doesn't exist in the relationship of a vector and its components since they cannot exist without each other. Theoretically, if you hooked up three three-phase generators in parallel, one with a positive sequence current output, one with a negative sequence current output, and one with a zero sequence current output, you could create an unbalanced set of currents. We don't normally do that. Instead, we have unbalanced load creating unbalanced currents. When a meter presents the magnitude and angle of a negative sequence current, it's measuring the actual current and doing the mathematical analysis.
Can we manipulate certain components of current independently? Yes, and that is the foundation of vector control in drives, inverters, etc., but that is a story for another time and involves resolution into the dq0 and αβγ domains instead of the ZPN domain.
I hope that clears things up.