Need help with t-min calculation on above ground storage tank
Leon Charles
Industrial
I'm having trouble with the t-min calculation for an above ground storage tank.
I followed instructions in API 653, but the final answer does not look correct, see below.
Tmin-?
D - 28.5'
G - 1.00
S - 24,900
E - .100
H - 45.9'-1 = 44.9'
Tmin = 2.6(H-1)DG/SE
Tmin = 2.6 x 44.9' x 28.5 x 1.00 = 3327.09 = 1.336
24,900 x .100 = 2,490
This t-min does not look correct because shell course #1 thickness is .250", sketch plate is .250" and and remaining floor is .312"
Dear Leon Charles,
All dimensions are in feet. What is the unit for 'S' ?
Regards.
DHURJATI SEN
Kolkata, India
Dear Leon Charles,
You made me calculate after so many years.
Take E = 1, you get tmin as 0.133"
Regards.
DHURJATI SEN
Kolkata, India
Dear Dhurjati Sen,
your answer to my t-min Question was very helpful.
Thanks,
Leon Charles.