Hi bentov
There are three major causes of SCR failure, one is excess current while the unit is running and that can be due to the magnitude of the current of the rate of rise of the current, and another is OFF state over voltage which once again can be related to an overvoltage (surge) or a rate of change of voltage (transient) and the last is thermal where the junction temperature has been allowed to operate above 125 degrees C for too long.
Failure during RUN is invariably a current problem which can be due to a voltage surge with high current going to the motor.
Failure during the OFF state is because the SCRs are blocking an excess voltage and this can be transient or surge in nature.
If the starter is bypassed, it is almost immune to current related problems during run and the current will bypass the SCRs and flow through the contactor.
So your major problems are in the OFF state and thermal.
The thermal situation is related to SCR (model) sizing and enclosure ventilation, so provided that both of these are correctly addressed, there should be no issues.
In the off state with a three pole device connected in series with the lines to the motor, the transient or surge must be high enough to cause a breakdown of two SCRs in series. For example where 1600V SCRs are used, the voltage transient must be over 3000V assuming reasonable balance in the voltage blocking of the SCRs.
In the case of a two pole device, the voltage transient must be above 1600V to cause a breakdown so these devices are much more prone to damage from transients than three pole devices.
If the motor protection operates and turns OFF the starter, one phase is left connected to the motor and if there is a leakage to ground, it will continue to draw current until fuses fail.
With a two pole device, you should use a contactor to disconnect the starter when not operating.
The regulations in some territories require that you disconnect all three live conductors from the motor.